Cold Form Webbed Floor Joist Minimum Wall Bearing Required
Cold Form Webbed Floor Joist Minimum Wall Bearing Required
(OP)
Any one can tell me what is the minimum wall bearing required as support for cold form floor webbed joist??
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Cold Form Webbed Floor Joist Minimum Wall Bearing Required
|
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
Otherwise, regardless of what any guide might have, you still need to determine or verify the bearing length on your own depending upon the reaction and what material you are bearing on.
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
I've seen cold-formed roof trusses, but, i've never seen cold-formed (diagonal) open-web floor joists.
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
http://www.newcastlesteelframes.com.au/userfiles/I...
please see the link , that what i am talking about the cold form webbed joist
reaction are about 21 KN and bearing wall is 150 mm wide so i can support my 2 webbed joist on it this mean 75mm wall bearing will carry each floor joist is this enough?
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
RE: Cold Form Webbed Floor Joist Minimum Wall Bearing Required
yes bearing wall is cold formed and studs are aligned with joists, yes there is a top track running.