Kitchen Hood Exhaust Insulation

Kitchen Hood Exhaust Insulation

Kitchen Hood Exhaust Insulation

(OP)
I'm installing a welded 16ga black iron duct for a commercial kitchen hood. Do I need to insulate the duct with firewrap. Wanted to make sure I'm reading the mechanical code correctly.

506.3. Grease duct clearances:

Where enclosures are not required, grease duct systems and exhaust equipment serving a Type I hood shall have a clearance to combustible construction of not less than 18"....

So if my grease duct is more than 18" away from any combustibles I don't need to insulate it?

My thought was to insulate with firewrap where I come through the roof then stop the insulation as long as I'm more than 18" from any combustibles.

RE: Kitchen Hood Exhaust Insulation

Yes, read the fire wrap manufacturer installation requirements, you may need to overlap or double wrap

knowledge is power

RE: Kitchen Hood Exhaust Insulation

Normal practice is to make a drywall lined chase for the duct with the required clearances. On roof penetrations , a ventilated chase with sufficient clearance to meet local code is required. Stop and think about what happens when that duct gets loaded with grease and catches fire.
B.E.

You are judged not by what you know, but by what you can do.

RE: Kitchen Hood Exhaust Insulation

(OP)
Should have explained the installation a bit better.

Building is about 18' high. Bottom of hood at 6'6", top 9'6". Wall hood is against ends at 10' high. Duct goes straight up from hood to roof. No combustibles within a few feet, except where we penetrate the metal deck at roof level.

RE: Kitchen Hood Exhaust Insulation

I recommend using the firewrap insulation from the top of the hood to the roof so it would serve as insulation to prevent condensation on the duct surface during winter when the hood is off.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources