What three test should be made to determined the condition of a cicuit breaker??
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: ask
RE: ask
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: ask
We usually conduct the following tests:
a) IR test in both open and close condition
b) Contact resistance measurement
c) Timing test
An additional test could be DCRM (Dynamic contact resistance measurement).
RE: ask
RE: ask
B phase contact resistance
c phase contact resistance?