What to expect on primary of delta-star (grounded) transformer with an L-G fault on secondary?

What to expect on primary of delta-star (grounded) transformer with an L-G fault on secondary?

What to expect on primary of delta-star (grounded) transformer with an L-G fault on secondary?

(OP)
I am a bit confused with the behavior of a delta-star (grounded) transformer with a line-to-ground fault on secondary.

Basically as I understand, fault current affecting faulty wye phase will induce a similar current on corresponding delta limb to sustain magnetic balance of the yoke. The confusion is about the line current in the delta side, would it be affected by the fault? or the induced current will tend to circulate inside the delta since its basically a zero sequence current that has no path outside the delta?

Any clue?

RE: What to expect on primary of delta-star (grounded) transformer with an L-G fault on secondary?

Well if it is three transformers in a bank, a line to ground fault will be a line to line load or fault on the primary.
If it is a three phase transformer with a three legged core the phantom delta may add some unexpected results.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: What to expect on primary of delta-star (grounded) transformer with an L-G fault on secondary?

If the fault current on the wye side is in only phase winding the it will also only be in one winding of the delta. No current in windings of the delta that don't also have corresponding current in the wye. Thus, a low-side line-ground fault on the wye shows up as a line-line fault on the delta side.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources