Using short piles for foundation of tall structure. Any shortcoming?

Using short piles for foundation of tall structure. Any shortcoming?

Using short piles for foundation of tall structure. Any shortcoming?

(OP)
Hi,

What's the general rule about using short piles for the foundation of tall building? The thing is the ground is neither good nor bad. 250mm square concrete piles only penetrated around 7m into the ground. With pile cap in place we are only looking at around 4.5m pile remaining in the ground supporting the structure. This is no longer so much a friction pile but rather end bearing pile.

Is it ok to use short piles or would I be better off switching to bored pile instead? Assuming over excavation of the ground does not happen and the piles remain in place. How about bearing capacity failure and heaving of the ground? Thanks.

Alex

RE: Using short piles for foundation of tall structure. Any shortcoming?

If the piles do not have to resist uplift (such as overturning moment from wind load), the length of the piles (within reason) should not matter. IMHO, 4.5 meter embedment for a 250mm pile is ok.

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Using short piles for foundation of tall structure. Any shortcoming?

You need to be sure that the soil below the piles can support the building weight without excessive settlement or even bearing capacity failure.

RE: Using short piles for foundation of tall structure. Any shortcoming?

Alternatively, did you consider using a mat foundation with ground improvement or over-ex / replace with engineered fill?

RE: Using short piles for foundation of tall structure. Any shortcoming?

In the above case a critical issue to consider mandatorily might be the stability of the whole pile group behaving as a block foundation, if there are substantial lateral loadings.

www.mccoy.it

RE: Using short piles for foundation of tall structure. Any shortcoming?

(OP)
Hi All,

The stricture is 7 stories high but the base is quite large. So lateral load issue would be minor in this case. My only concern with short piles as aeoliantexan pointed is the strength of the soil underneath to prevent bearing capacity failure. The piles were driven to set so they are founded on very good soil. We will be doing a static pile load test to confirm the capacity and settlement.

We have also decided to set a minimum depth of penetration of 9m for driven piles (before pile caps) and anything shorter than that we will opt for bored piles instead.

The soil we have here in Brunei is highly heterogeneous (if there is such a word) and hence to over excavate and replace with engineered fill for a raft foundation may not be a good way to go. Plus we have not used raft foundation before, experience wise we are kinda short on.

Anyway, thank you for all your responses and will update here when the load tests have been conducted with good results.

Alex

RE: Using short piles for foundation of tall structure. Any shortcoming?

There are many dangerous comment in this thread.

You should make a settlement analysis. (Imaginary footing method, for example.) Then, you should decide on the length of your piles. If settlement is ok and if your piles are safe against the building load (if not increase pile length or diameter) you can go on.

RE: Using short piles for foundation of tall structure. Any shortcoming?

i would expect you have a soil investigation done that way you can know what material underlays where your piles are terminated.

RE: Using short piles for foundation of tall structure. Any shortcoming?

Appears that you will be installed piles to bedrock (it may be soft or hard rock). If you use short driven piles I would be careful on selecting the correct hammer size to avoid structural damage in the piles. Geotechnical capacity may be higher than the structural capacity if you install piles to bedrock so monitor the installation to avoid structural damages. Along with your static test, you can also specify dynamic testing for checking capacities and pile structural integrity.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close