Water District has provided HGL's how can I convert this to available flow?

Water District has provided HGL's how can I convert this to available flow?

Water District has provided HGL's how can I convert this to available flow?

(OP)
I will be designing a fire sprinkler system for a new office building in Downtown Las Vegas, and hydraulic flow tests are no longer allowed. I have been given HGLs for the intersection of an 8" and 6" pipe, but I do not posses the know how for converting this to the Static, Residual and flowing pressures I am accustomed to. Please help if you can. I have attached the information for review.


Thanks!

RE: Water District has provided HGL's how can I convert this to available flow?

Interesting, not an engineer so cannot help you.

https://www.cityofnorthlasvegas.com/Departments/Ut...


Suggest you contact one of the fire protection engineer firms that works in Las Vegas

RE: Water District has provided HGL's how can I convert this to available flow?

You know the static head at 50 psi on one hydrant, therefore, that pressure will be on straight line on a semi log hydraulic graph where Q^1.85 power is represented on the absissa. Q is in GPM and the ordinate is the pressure in psi. Assume at least one flow rate in GPM between that hydrant and a next one, then, knowing pipe length including equiv. length as well as pipe diameter calculate pressure drop via Hazen-William formula with a C value corresponding to piping age. Plot the friction loss as a straight line on same graph starting the line at 0,0. Subtract static head line from friction line and the resulting line which probably be no longer a straight line will be you water supply at the 50 psi location. Since the city will probably require a minimum 20 psi at hydrants at that 50 psi location you can determine that approximate amount of water at the 20 psi residual pressure. Note if there is significant difference in elevation between your two hydrants, the 50psi line will have to be adjusted accordingly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources