2 MVA transformer Excitation Current Issue
One of two new, identical, 2 MVA, 4.16kV-480/277V delta-wye, KNAN transformers has unusual excitation current tests results prior to energization. Both transformers passed factory tests and most of the usual NETA field tests: insulation power factor (Doble), insulation resistance, TTR, winding resistance, oil test etc.
Following standard Doble procedures, the single phase excitation current was measured. One transformer had no issues but the test set could not build current on unit #2 when trying to energize H1-H3 or H3-H2. Test set would trip. H1-H2 was OK.
A transformer degaussing test set was used to demagnetize the core with limited success. The Doble excitation test set was only able to build up to 100V before tripping. Prior to demagnetization, it could not get even get to 10V.
Our testing company thinks the transformer is going to blow when energized. The manufacturer, a very reputable supplier, says to energize the transformer and that the excitation current test is of no concern. They point out that individual excitation current tests were not specified and are not part of the typical IEEE standard tests. The factory engineers say they have seen this before where two sister units have different excitation currents but were placed in service with no problems. They do not have an explanation as to why there is a difference.
There is no indications of physical impact or damage that might have moved the core or caused magnetic anomalies.
On the good unit, typical excitation current readings at 1.25kV:
H1-H2: 0.49 A, 3.6 kW. H2-H3: 1.05A, 7.97kW. H3-H1: 1.1 A, 7.9kW
Suspect unit tests at 1.25 kV and 0.10 kV:
@1.25 kV: H1-H2: 0.47 A, 3.5 kW. H2-H3: tripped. H3-H1: tripped
@0.100kV: H1-H2: 1.13 A, 4.37 kW. H2-H3: 5.96A, 52.7 kW. H3-H1: 2.56A, 8.61 kW
Factory tests results show 3-phase no load loss at 2kW and excitation current at 0.2% = 4.8A @ 4.16 kV (about 1.45 A @ 1.25 kV)
I tend to go with the manufacturer, they are guaranteeing it. But it would be nice to see an explanation before closing the breaker.
Have you seen any anomalies like this on new units? Could single phase versus three phase tests be skewing the results?
RE: 2 MVA transformer Excitation Current Issue
This is the most reliable and consistent test available for transformer engineers to check the healthiness of transformers since Doble standardized it during 1960's.
Muthu
www.edison.co.in
Do you have access to a 3-phase Variac? It doesn't need to be a big one, 10A or so per phase is sufficient. Feed the HV winding with the balanced 3-phase supply from the variac and increase gently from zero. Connect an ammeter in at least two phases, and for preference in all three phases in case there's a path to earth. Observe what happens as you increase voltage.
I realise that it may not be possible to do further testing, but have you considered degaussing the core and then doing your single phase test starting on a different winding.
That is, see if the issue is related to the order in which the phases are tested individually. Sort of like rolling the connections to isolate a problem.
Bill
"Why not the best?"
Jimmy Carter
Tested following standard Doble procedures? Forgive me for assuming the test set used was Doble M4000.
Post indicates tested at 1.25kV. Maybe it was calcultated to 1.25kV?
Doble says: "Excitation-current measurements should be performed at the highest test
voltage possible within the range of the set, but should never exceed the
voltage rating of the winding across which the test voltage is applied."
Doble emphasizes that statement in bold.
Is there any kind of tap changer? DETC or LTC?
According to Doble there should be tests for NEW equipment as follows:
"Load Tap Changers
New - 1L, N, 1R, 2R, … , 15R, 16R (18 tests/phase)
De-Energized Tap Changers
New - A, B, C, D, E (5 tests/phase)"
Perhaps you omitted the information to shorten the post or I am out of date with new Doble procedures.
My first guess would be that the phase NOT under test is not properly grounded or the neutral (X0) on the LV side is not properly grounded when performing the tests. Or it could be an internal or cable problem with the M4000.
If everyone is confident it was tested correctly and the manufacturer says its ok to energize, be sure to have some kind of written ok from the manufacturer.
Not sure that it is possible or would even help but a SFRA test is a good way to "look" inside a transformer. And having a sister unit offers an excellent comparison.
Best of luck.
The factory results are not to be considered for comparison, there is a published whitepaper dealing with that.
Look for a copy of Doble Test Procedures, 72A-2244 Rev A. The new version is on their website is password protected.
And, Transformer Excitation Current Test Procedures - Doble Engineering Diagnostics Toolbox
Our testing contractor is very experienced with Doble testing and did all tests per the procedures: all DETC taps, etc. I didn't post the full test results, just a summary and converted the mA & W to A & kW. The results were sent to Doble for analysis. Their engineer suggested further testing, SFRA & Leakage Reactance. SFRA tests would not tell us much unless we could also dismantle the bus duct and HV cabling on the sister unit to get a comparison test. I'm investigating what test equipment is needed for a leakage reactance test.
Our management is evaluating the cost and time delays of further testing against the risks of energizing a unit that the supplier guarantees and says they can replace in three weeks. (Removal and replacement time not included). If it does fail, the other unit can supply the project's power needs for commissioning. Cost of testing is approaching the cost of the transformer when air freight of equipment, travel time, support labor etc is included. Also, if the testing contractor is retesting the transformer, his engineers are not testing the other equipment needed for energization. I'll know more when I get to site tomorrow.
Thank again for the background and advice. Safety has to be priority #1.
No other indication of problems. Transformer was isolated, but X0 was grounded. Test was only 10-15 minutes. We were unable to get access to the LV terminals to try LV excitation tests.
We repeated the test on the identical transformer which only drew 0.2A on all three phases.
Details:
H1: 278.0V @ 0°, 0.20 Amps @ -60°, 0.03 kA, 0.13 KVA
H2: 279.V @ -240°, 5.2 Amps @ -275°, 0.63 kW, 0.71 kVA
H3: 277.8 V @ -120°, 5.1 A @-90°, 0.66 KW, 0.72 kVA
Total Input: 1.32 kW, 1.86 kVA.
LV Terminals: 55.4 V phase-phase, 33 V phase-neutral.
That 1.32 kW loss translates to about 11.2 kW at full voltage (4.16 kV) if everything is linear. No load loss would be around 60% of the anticipated full load losses. I expect that much heating would eventually do some damage.
We will see what the supplier wants to do.
Hopefully you or the owner can reject the unit. Or the supplier does the right thing and replaces it without question.
Reversed polarity of one or two phases?
A baker surge comparison test might be informative.
Muthu
www.edison.co.in
Looking at the data from the LV test, I am thinking there is a turn-turn short or other issue in the H2-H3 or X3 winding. Currents into H2 & H3 are 180 apart and essentially in phase with the H2-H3 voltage. Normal excitation current would lag voltage by 90 like the current into H1 lags the H1-H3 voltage by 90 degrees. (Test voltage connections ended up phase rotation H1, H3, H2).
TTR tests look OK except one winding's ratio is high by about 0.004 or 0.02% compared to others but still within stadard limits. Not enough data to support the turn-turn fault theory.
(Ratio = 14.253, read 14.301, 14.301, 14.306. Ratio = 15.001, read 15.006, 15.006, 15.008. Ratio = 15.390, read 15.400, 15.401, 15.404.)
The construction power voltage was varying during the test, making it difficult to get high accuracy voltage readings on the LV windings. With the repair shops steady and controllable test voltage we should be able to do more troubleshooting.
Meanwhile we are energizing the facility on the other unit for now.
I hope you got the cranky one, because electronics ones with no knobs to adjust the ratio tend to give different readings in two consecutive tests.
"1. By time I got there they had done ratio test on Tap C . (H1H3 – X0X1 15001, H1H2-X0X2 15003, H2H3-X0X3, 14.993)
2. We removed the tops and inspected the inside, nothing stood out, oil is very Green.
3. We energized using an Aux Wye-Delta utility transformer to hi side. (Used another transformer to step up the voltage applied to H1, H2, H3)
Step 1 : they applied 35 Volts to low side of aux transformer, measured input current : 0.6 A , 1 A , 2 A .
Step 2 : they applied 60 volts to low side of aux transformer, measured input currents : 15 A, 17 A , 30 A. Phase C continued climbing and smoke started to come out .
4. They drained the oil half way below connections and energized it again to spot where smoke is coming from, it appeared that lead connection to tap changer on Phase C was the source of smoke."
As many of you pointed out, there was an issue in the tap changer connection. (DETC). Should be back in service next week.
Thanks for the input!
Bill
"Why not the best?"
Jimmy Carter
After the on site test at 10% voltage (480V 3 phase on 4.16kV winding) showed a relatively large in-phase current on the H2-H3 winding, we were pretty certain we had a turn-turn or tap-tap fault, most likely at the DETC tap changer or the cable termination block.
I'll post what we find.
No details were provided on how the tap changer connection was "bad" or the actual failure mode. If it wasn't damaged during transit or during installation, how did the unit pass the factory tests?
More information to follow.
On site tests after repairs show good excitation currents but a >10% variation in winding resistance measurements and marginal insulation power factor. Repair shop test results show the resistance of individual HV coils were very similar before they were wired in delta. Another connection issue?
We are concerned that the same FR3 oil was apparently used without processing. It now has a few ppm of acetylene and high moisture content. Insulation power factor is high, probably due to the contamination and water in the oil. (I hadn't realized that FR3 oil pulls moisture out of the cellulose windings unlike "normal" transformer oil that puts the moisture in the windings).
Our client is concerned about having a "new" transformer with marginal quality oil and suspect winding resistance readings. We are still fighting the vendor, who claims since equal resistance, or minimum quality of oil, or power factor tests were not specified, the unit meets our specification. I'll let our lawyers work that out.
I appreciate the advice we got on this site. Had we not followed the advice and energized it, that failure would have been a lot larger. (But maybe I would have gotten a new transformer?)
I don't believe I want to buy from this supplier again, at least not this facility.
Keith Cress
FR3 must be filtered to remove moisture. But don't be carried away by the talk of esters drying out paper in transformer. The difference between esters and mineral oil is that water solubility in esters is nearly 10 times more than that in mineral oil. So when mineral oil contains 35 ppm of water, ester will carry 350ppm. But remember paper in transformer will carry 1-2 % of water by weight. So in a 10 MVA transformer(of say 10,000 litres oil + 1000 Kg paper ) The paper will carry 10Kg of water and mineral oil 0.35 Kg of water. With ester it will be 3.5 Kg of water in ester + 7.5 Kg in paper. So ester may reduce the water content in paper by approx. 30 %.
Thanks to all the resources we got from the experts on this site, our Lead Electrical Engineer was able to put together a good case and get it to the right manager at ABB. They are building a new transformer at no cost. The repaired unit can become a spare for our client. One of the final convincing arguments was the comparison of the oil sample tests from the four similar transformers. Three samples from the units under load looked great and the fourth looked like it needed immediate maintenance even though it wasn't energized yet. Not good for a "new" facility.
A commercial issue created communications problems that probably drug out the discussions. Our company bought the transformers as part of a blanket agreement that included these smaller transformers, switchgear, bus duct, control houses, MV & LV MCC's. Our vendor was between us and the manufacturer. We may have gotten faster resolution sooner if we had a direct commercial relationship. On the other hand maybe our vendor's commercial clout with that factory finally brought resolution, once we got the right story to the right people.
Once again, after 40+ years in electrical work, I found out there's a lot of things I still need to learn about transformers, testing, and electrical engineering. And this site is a great place to do that!
Thanks for the follow-up too.
Keith Cress
Thanks for the closure.
Yours
Bill
Bill
"Why not the best?"
Jimmy Carter