Vent lines for Oily Water Sewer system

Vent lines for Oily Water Sewer system

(OP)
I am working in a Refinery project . The project specification for underground drainage for Oily water sewer system says that " Vent shall be installed in the following locations (1) upstream of the first sealed Manhole in a Oily water drainage system ( 2) Down stream of the farthest catch basin (3) Those section of the drainage line located between liquid seals.
Can anyone explain why the vent should be installed in the upstream of the first sealed Manhole. The Oily water sewer system consist of a number of catch basin connected into a main branch which drains into a manhole .Like that Manholes are connected one by one and draining out of battery limit. My question is that if the downstream of catch basin have a vent then why again on the upstream of the Manhole. Is it to protect the water seal of the Manhole?

RE: Vent lines for Oily Water Sewer system

Nabeel3

As the liquid naturally moves from upstream to downstream manhole, it will tend to induce a small draft thereby potentially inducing some ventilation when there is flow.
Likewise any gas that is released that is lighter than air will tend to move up the slope of the drain to the upstream manhole and can then be vented if necessary.

Regards
Ashtree
"Any water can be made potable if you filter it through enough money"

RE: Vent lines for Oily Water Sewer system

Gravity sewers are designed to be partially full, not full pipe flow. Should the sewer be surcharged (meaning full pipe flow), then a siphon will occur. You would need to vent the upstream manhole.

If the sewer pipes were oversized so that the sewer would never surcharge, you could probably do away with the upstream vent.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close