Hi ,
i am asking about transformer's temperature
There is any correlation between the Winding's temperature and (Var) which generated by the Generator?
for instance i have to case with same ambient temperature :-
the first, i generate (150MW) with (5Mvar)
the second, i generate (150MW) with (15Mvar)
there is any difference on the winding's temperature for the transformer?
with regards
i am asking about transformer's temperature
There is any correlation between the Winding's temperature and (Var) which generated by the Generator?
for instance i have to case with same ambient temperature :-
the first, i generate (150MW) with (5Mvar)
the second, i generate (150MW) with (15Mvar)
there is any difference on the winding's temperature for the transformer?
with regards






RE: Transformer's Temperature
the second, i generate (150MW) with (15Mvar) -- 150.75 MVA = 1.00446 greater current, 1.009 greater I
2R lossesthere is any difference on the winding's temperature for the transformer? Probably not enough to measure.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Transformer's Temperature
RE: Transformer's Temperature
RE: Transformer's Temperature
Bill
--------------------
"Why not the best?"
Jimmy Carter