Testing Compressive Strength of High Strength Gypsum used in ASTM C617 by way of ASTM C109
I work in a concrete material testing lab and we have to test 2 inch cubes of high strength gypsum as proof tests for C617
ASTM C617 in Section 5 (materials) 5.1.3 says to test the compressive strength of 2 inch cubes in accordance with C109. Does anyone know whether a flow test needs to be done for high strength gypsum, since it isn't mortar? Or do I just skip down to 10.4 Molding the Specimens? I have to comply with the C617 testing of high strength gypsum capping material every 3 months, or every new batch. If anyone out there uses C617 to test high strength gypsum paste for the purpose of capping cylinders or cores in a material lab, any additional information would be appreciated. My general understanding is that I just need to establish tests that show water/cement ratios along with a few time increments to prove that it reaches the 5,000 psi or cylinder strengh, whichever is greater requirement.
RE: Testing Compressive Strength of High Strength Gypsum used in ASTM C617 by way of ASTM C109
Use only the parts of C109 that apply to the actual test. Flow is not a consideration for your application so I would ignore that. C109 gets specified as a testing method in quite a few ASTM standards, even though its primary purpose is for portland cement.