Snow Load Reduction due to Grating
All,
I've recently read this thread http://www.eng-tips.com/viewthread.cfm?qid=291105 about snow loading and grating and there does seem to be a mixed opinion on it.
I'm currently desiging a frame system to support a MUA unit for a soccer field. The platform is to be 16'-6" x 27'6" x 8'-0" high and placed against a much higher structure. Through some very quick snow drift calculations the inside edge would accumulate a snow load of approximately 80psf and the outside edge to be quick significant as well as it would drift against the MUA unit.
My question is weather I should account for this or not or have a reduction factor at least for the snow load.
My factored weight of the unit is 55psf assuming 10psf dead load for the structure.
Now I'm questioning for my live/snow load if I should calculate 1.5 * 20 psf Live + 0.5 * Snow Drift Loading or can eliminate altogether.
Any opinions would help.
RE: Snow Load Reduction due to Grating
Is there any heat coming up from the grated area, like a transformer vault?
Mike McCann, PE, SE (WA)
The only heat that may occur is heat loss from the Make Up Air Unit.
Thanks for the Help!
But maximum wind will probably not occur at the same time as shoveling.
the authors state in reference to snow on grating that "balanced snow will accumulate on this surface just as it would on a checkered plate or any other continuous flooring material". They further state that snow drift should be considered.
I've also seen snow accumulate on grating as if it were a solid surface.