Fire Hose Valve Height?
Fire Hose Valve Height?
(OP)
Anyone know what the requirements are for the height of a hose valve station on a fire stand pipe and where I can find said code?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Fire Hose Valve Height?
7.3 Locations of Hose Connections.
7.3.1* General.
7.3.1.1 Hose connections and hose stations shall be unobstructed and shall be located not less than 3 ft (0.9 m) or more
than 5 ft (1.5 m) above the floor.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...