Connecting a Sink to Fire Water Line

Connecting a Sink to Fire Water Line

Connecting a Sink to Fire Water Line

(OP)
I'm working on a small 500 SF pump station on an airport, and the owner wants a service sink the building. The civil engineers want to tap into the fire hydrant loop just outside the building for the sink and label everything non-potable.

I've never seen this done before, but I can't find anything in the code the strictly prohibits it. It just sounds like a bad idea. Any input would be appreciated. Thanks.

RE: Connecting a Sink to Fire Water Line

How is this different then every street in America with a fire hydrant and public water supply tied together? Now if that fire line is connected to a fire pump, operating the sink may turn on the fire pump depending on how close the sink is to the fire pump and flow of the sink.

RE: Connecting a Sink to Fire Water Line

Just calling (labeling) it as non potable does not make it so.

Typically, in non residential applications, a reduced pressure zone (RPZ) will be required to protect the municipal source from anything. Typically, a second backflow preventer (usually another RPZ) would be downstream to use the water as non potable. In this case, since there are no other water uses, only one RPZ would likely be required.

Service sinks (and hose bibs) are a historic (and notorious) culprit for back siphonage and or backflow contaminating municipal services.

In the IPC areas, 602.2 indicates that potable water shall be supplied to all plumbing fixtures.

RE: Connecting a Sink to Fire Water Line

Also consider the possibility of needing a water meter, backflow preventer and pressure reducing valve. If it is a fire loop it might have high enough pressure to blow up your plumbing devices.

as LCREP said if the line is a dedicated fire loop you might be in for a surprise if you plumb this sink.

RE: Connecting a Sink to Fire Water Line

In addition to the backflow issue, how does the water purveyor feel about the proposed tap? The utility I work for might consider the tap a theft of service. We generally handle metering and billing of fire loops different than ordinary domestic taps.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources