4 tanks - 1 mat foundation?
I have 4 tanks. Tanks will be full of fluid, size is 32' high and 15.5' diameter.
I'm taking over this design from another engineer.
He has 1 mat foundation for all tanks, mat size is 80' x 24'.
I'm concerned if this will cause issues with differential settlement if one or few tanks are either empty or full.
Shouldn't this be addressed in Geotech report.
Geotech report only suggests use drilled pier for large vertical loads with a bunch of formulas for drilled pier axial capacity.
I don't even know why the original design is only on mat foundation and not on deep foundation but that guy is gone now so I can't ask him.
RE: 4 tanks - 1 mat foundation?
Sounds like he ignored the geotechnical report. Likely if a single mat had been feasible, the geotechnical engineer would have noted that. Considering he/she recommended drilled piers for the tanks, there are likely soil conditions below that would be detrimental to a mat foundation. You might consider a pile supported mat if you're concerned about differential settlement.
A talk with the geotech might clear up some things.
The mat could have been part of a containment system for the tanks.
If one tank is empty and others full- that would not generally be addressed in the soils report, other than to give you a subgrade modulus or something like that; that would be assumed to be elastic deflection, not differential settlement.
I have done several mat foundations with multiple tanks (90' tall- 12' diameter) on them and haven't had any differential issues. We have had really good allowable bearing pressures (5 ksf+) though, so that helps. The geotech has always been really instrumental in what we do so I second Ron's comment. One item to add is a discussion with the owner to determine what their operational loading will be. My projects have been in the dairy industry so the fluid levels are really dynamic and there isn't really the "time" for settlement to occur unless a tank goes offline.