Reforcement requirements for topping slabs?

Reforcement requirements for topping slabs?

Reforcement requirements for topping slabs?

(OP)
We're locating equipment on top of an existing slab. The existing floor slab is 6'4" thick with an 8" non-sloping topping slab on top. The new equipment has the potential to spill and we believe it will be more economical to add another 6" topping slab (sloped) on top of the existing topping slab and cut drainage trenches in the existing topping slab. What is the minimum required reinforcement for this new topping slab? ACI 318 has minimums in section 7.12 but this slab won't be structural.

RE: Reforcement requirements for topping slabs?

A fully bonded overlay does not need reinforcement. A partially bonded or unbonded overlay does. Since the new 6" overlay will be sloped and the underlying concrete is level, I assume thickness will vary from 6" to a smaller value. Reinforcing concrete less than 6" thick is tricky. Probably best to go with a fully bonded overlay and no reinforcement.

See the Portland Cement Association paper Resurfacing Concrete Foors

www.SlideRuleEra.net idea
www.VacuumTubeEra.net r2d2

RE: Reforcement requirements for topping slabs?

Whether the topping is bonded or unbounded, it has the potential to crack. This could occur as a result of movement in the base slab or perhaps an impact force on the topping slab. If you are concerned about the integrity of the topping with regard to spills, I would add reinforcement to minimize the potential crack width. For slab toppings with reinforcement, we usually use steel fibers (industrial projects)

RE: Reforcement requirements for topping slabs?

(OP)
SlideRuleEra: Thank you for your response and great attachment

MotorCity: This is an industrial project. Are the steel fibers you use a specific WWR?

RE: Reforcement requirements for topping slabs?

Will the drainage trenches cut into the existing topping be lined with waterproof material?

BA

RE: Reforcement requirements for topping slabs?

We use steel fibers or WWF, not both. Using both in a thin topping would make it nearly impossible to place and finish the concrete properly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources