Retrofit Lintel in CMU wall with Loose Fill Insulation
All,
So interesting problem here. A client wants to create a larger opening (existing 3'-0"x7'-0" door in 3'-4"x7'-4" masonry opening). They want to go to 5'x7' (5'-4"x7'-4" masonry opening), IE (2) 30" doors. It's a single wythe exterior 8" CMU wall with #6 bars at 48" o/c and (2) each side of opening (I bet they only installed one in the field, but the drawings called for (2-#6) each side of openings). Anyway, it also has LOOSE FILL insulation, (Fun times!) Wall is just painted on the exterior. Also, it is load bearing, but not much.
A few questions arise:
1. Typically, I like steel lintels for retrofit, but here I'm thinking a 16" deep bond beam with one more course toothed in. Anyone successfully tried this before? Channel above as "temporary shoring". Reason I'm thinking CMU lintel is the insulation issue.
2. I'm concerned that all the loose insulation is going to pour out of the wall during construction (after they take out the CMU to install the new lintel). Has anyone found a good way to prevent that?
3. I think this is an egress door, and I'm not sure that (2) 30" doors will cut it. I'm somewhat putting on my architect hat here, which I don't want to do, but I also want to advise the client that he needs to maintain egress requirements. There are only (2) exits (this is one of them) and I'm thinking you need (2) accessible for retail space (2009 IBC here), which I think means a 3'-0" door. Anyone dealt with this?
4. Lastly, I'm thinking "flashing". I've never been a big fan of block-filled and painted CMU as the only waterproofing, but it's done a lot around my parts. Especially if I go the steel route. Any ideas/thoughts?
I'm at the point where I may tell the client it's could be a bit more involved/expensive than he had hoped, because he was on a somewhat tight budget, albeit reasonable. Thanks to all!
RE: Retrofit Lintel in CMU wall with Loose Fill Insulation
The core fill is a tough one. My gut tells me it wouldn't fall out but I've no anecdotal evidence to substantiate that. I suppose you could use HY70 screen tubes without the anchors to block off the cells but that seems like a lot of effort to go through to preserve insulation in an area where the door frame will be a pretty significant thermal break in its own right.
As for the door, I'm just planning to advise the client to look into with an Architect as needed.
BA
You can use an IR thermal camera and see voids if needed if only half the height empties.
building a bond beam like that is not easy... if it even accomplishes your intent of keeping the insulation in place
Thanks to all!