Fault current ground path

Fault current ground path

Fault current ground path

(OP)
How come I never see the impedance of the earth in fault current calculations? If you have a fault, doesn't it have to makes its way in the ground back to your ground source or sources? I see stuff associated with creating a low effective fault paths in the NEC but nothing elsewhere for higher voltage stuff like in distribution and transmission. Is earth that great of a conductor for fault currents?

RE: Fault current ground path

Earth resistance is accounted for the line Z0 impedance calculations.

RE: Fault current ground path

It's an additional resistive component added to the impedance. Carson's paper derived a terrible series formula for approximating it based on frequency. Fortunately, at 60 Hz, you just add 0.0953 ohms/mile.

RE: Fault current ground path

(OP)
In one of my text showing modeling a line with the return path, it shows the term, De = 658.368 *(rho/freq)^.5, inside of a logrithmic function for Zij. So, there would have to be a lot of variation in the impedance of the ground return path I imagine before anyone started caring about the soil resistivity enough to test it.

RE: Fault current ground path

I believe you're correct... I've only ever assumed 100 ohm-meters in my world. As you get higher resistivity (thousands of ohm-meters), longer transmission circuits, you should give it a little more consideration. Unless you're in an area of known higher resistivity, I don't know that it's worth looking into.

RE: Fault current ground path

100 ohm-meters may be much too high. I get a much better alignment between model results and actual faults with 10 ohm-meters. Too high a resistance number and you find your ground elements reach too far.

RE: Fault current ground path

The IEEE Std 80 consider the split factor to determine the current path into the earth and the one to travel in the metallic return such as the shield wires of the line, neutral, etc. It is not unusual to consider a 50% fault current travelling into the ground.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources