Ventilation Requirements for Electronics Manufacturing

Ventilation Requirements for Electronics Manufacturing

Ventilation Requirements for Electronics Manufacturing

(OP)
I am looking for help in determining the ventilation requirements for an electronics manufacturing facility. I am used to using ASHRAE 62.1 but I do not see any space type that fits well with the operation in this facility. Anyone have any experience with this type of building?
Thanks

RE: Ventilation Requirements for Electronics Manufacturing

"Electronics manufacturing" covers a really wide variety of operations. Circuit board manufacturing? Soldering? Need much more detail.

RE: Ventilation Requirements for Electronics Manufacturing

Like Ross ABQ said, more information is needed.

In the meantime, ASHRAE 62.1, Table 6.2.2.1 has a line for "General manufacturing (excluding heavy industrial and processes using chemicals)".

Any processes that use chemicals will probably need a specialized and dedicated exhaust system, so handle those on a case-by-case basis; get this information and any other special requirements from the owner.

EDIT: You would get more response if posted in the HVACR forum.

RE: Ventilation Requirements for Electronics Manufacturing

As a user rather than an HVAC engineer, our facility had a lot of local exhaust ventilation on the manual soldering lines, automated reflow soldering and solvent wash (perhaps less common these days), and similar areas. As a result the makeup air flow was pretty high, although demand on the intake heaters was moderated by the heat output from the process which would otherwise have required cooling. As I remember it - from a good few years ago - the air filtration plant worked hard and required a fair bit of maintenance, although the detail of whether that was recirculation or fresh air intake filtration now escapes me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources