Compression Piles
Compression Piles
Compression Piles
The way I read the IBC 2012, there is still a way for you to have the reinforcement in a cast-in-place, concrete pile terminate at a point (and just have a single bar going down the center) where the pile will always be in compression only and has little moment. (I've typically fought this approach.)
But in the AASHTO code, I really don't see a way to do that. It appears to me that you need the 1% minimum at just about all cross sections. For those of you familiar with this code (and I don't have the latest): is that how you see it?
Thanks.
RE: Compression Piles
I design cast in place piles using the IBC and always use a partial length cage and full length center bar, except in high seismic zones where liquefaction may occur at the interface of soft/hard zones (in which case I may extend a four bar deeper). Per the IBC you only need the full cage to the point where the ultimate moment is less than the cracking moment (they provide a formula for this). I typically take the cage slightly beyond this point depending on the required shear reinforcement.
FHWA has publications on the design of piles which is fairly helpful. Looks like they don't have a download link for the pile design docs though - the drilled pier design doc is available for free. http://www.fhwa.dot.gov/engineering/geotech/librar...
For auger cast piles, the center bar is used to pop the bottom of the auger open to start the casting of the grout into the excavation under a minimum pressure head. Once the auger is removed, a rebar cage is pushed into the top of the fully grouted pile around the full length center bar. Anything more than a 10ft deep cage is frowned upon and it can be expected that for some of the piles, the full cage will not be all the way inserted (plan for it).
A drilled pier, which has a minimum diameter of 30" for skinny geotechs and 36" for our area, is fully excavated. The rebar cage is placed (I've always detailed a minimum of 4 full length bars for piers below the laterally loaded length and a full cage for lengths that will receive bending). and then the concrete is dropped into the hole. If a casing is needed, it is slowly removed under a concrete pressure head.
IBC makes a distinction between the pile length that needs to resist lateral and bending - must be reinforced like a column, and the rest of the foundation length. This is further extended as it relates to the building's Seismic Design Category.
For AASHTO, the FHWA docs should help clarify.
Thanks for the feedback and the link Teguci.
In Circular No.10 (at that link), section 16.3 says: "Furthermore, the minimum longitudinal reinforcement area in the portions of the shaft that behave as a column should be not less than 1% of the gross concrete area of the shaft. Below the section where the drilled shaft behaves as a column (i.e., is laterally supported) nominal longitudinal reinforcement may be provided. However, 0.5% of the gross concrete area of the pile is suggested as a practical minimum."
In section 16.6.1 (Axial Compression), it says nothing about being able to use a percentage less than 1%.
And the sample pier design (see Appendix A and Figs. 16-7 & 16-8) does not eliminate the longitudinal reinforcement at any point. This leads me to believe that a pier seeing AASHTo type loadings should have these minimum percentages at all depths
Can anyone who does AASHTO design regularly confirm this interpretation (from your experience)?