Water washing 316 valves

Water washing 316 valves

(OP)
Gents,

First time posting here so please be gentle
I have a valve which has been taken out from a clean propane gas service for inspection purposes. There is no corrosion but a mechanical failure upstream has left the valve covered with debris and dirt. Operations would like to water wash the valve using plant demineralized water before returning to service.
Valve has 316 body and operates around 40-50oC.
My fear is that the demin water may contain enough chlorides to cause chloride pitting corrosion when returned to service.

What precautions should be taken to water wash these valves?
What chloride content is acceptable for a demin water wash? I am seeing 50ppm and 100ppm max in API 510 and API 598 respectively.

Thanks

RE: Water washing 316 valves

Anything below 50ppm should be plenty clean. Though washing and drying is the easiest, after all you don't want any water back into your system.
Will water clean it or will you need detergents or solvents as well? Either way make sure that it is dry (even inside) and you will be fine.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube

RE: Water washing 316 valves

(OP)
Ok thanks Ed. Is there any guidance note/standard on water washing of pressure equipment that you know of? for example in shutdown and the internal walls of a vessel/exchanger need cleaning down to allow inspection?

RE: Water washing 316 valves

Demineralized water by definition is free of chlorides.

RE: Water washing 316 valves

You never know how good peoples water is.
It is best, and easiest to monitor conductivity, as long it is less than 4 microS (resistivity greater than 25MOhms) you should be good.

= = = = = = = = = = = = = = = = = = = =
P.E. Metallurgy, Plymouth Tube

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close