Power Cables and Communication Cable Distance Code Reference
Hey everyone,
This is my first post on this forum so hello to all! I have read a ton about the separation of power cables and communication with various "rule of thumbs" on the distance between for optimal reliability. Can anyone point me to the code reference for this rule of thumb? Is it NEC, IEEE or...
Thanks in advance,
Chris
RE: Power Cables and Communication Cable Distance Code Reference
NEC 70 is a good reference for power cables. The voltage defines the required separation distance.
For communication cables you have to trade off speed for distance. Check the communication standard (usually Google is a good start) and it will give you a starting point for speed vs distance limitations.
Z
Also, one rule in the NEC is that if the conductors occupy the same space, the insulation rating must equal or exceed the highest voltage insulation rating. That's often problematic for comm cables because it generally means 600V insulation, and often that isn't the case if nobody has paid attention.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
