Emergency Eye Wash Water Flow
Emergency Eye Wash Water Flow
(OP)
I am designing instantaneous electric water heaters for an army guard unit hanger that has 6 eye washes, installed 15 years ago.
These are just Eye washes, but when measured they are flowing 3 GPM, in lieu of the .4 GPM minimum?
Pressure in the building is 63 PSI.
Maintenance is hesitant to reduce the flow to the eye wash claiming they may not achieve the correct stream characteristics.
I called Bradley and Haws, asked if these units should operate correctly at .4 GPM, lots of evasive answers.
Has anyone had this experience?
These are just Eye washes, but when measured they are flowing 3 GPM, in lieu of the .4 GPM minimum?
Pressure in the building is 63 PSI.
Maintenance is hesitant to reduce the flow to the eye wash claiming they may not achieve the correct stream characteristics.
I called Bradley and Haws, asked if these units should operate correctly at .4 GPM, lots of evasive answers.
Has anyone had this experience?





RE: Emergency Eye Wash Water Flow
Why would you attempt to reduce the flow?
Mike Halloran
Pembroke Pines, FL, USA
RE: Emergency Eye Wash Water Flow
You need to provide enough flow to wash away the contaminant, but you also need to keep the velocity of the wash water low enough as not do further damage to the eyes.
I went thru this several years ago, depends on what you actually call the wash station, as an "eye wash" station has different requirements than an "eye/face wash" station.
Hope you find the link helpful, MikeL.
RE: Emergency Eye Wash Water Flow
Take a look at the instantaneous water heater information. They should have a minimum turn on flow. If you need 0.4 gpm, there are heaters rated for that.
Personally, I would not go down to 0.4 gpm if that is what the existing are flowing. Pick a heater that will work at that flow rate.
RE: Emergency Eye Wash Water Flow
There should be a test gauge to check the water flow: Water flow covers area indicated on test gauge at no more than 8” above spray heads. Contact the manufacturer.
RE: Emergency Eye Wash Water Flow
I should have mentioned that I did check the old O&M manuals to verify these units are indeed Eyewash only, and not Eye/Face wash.
Reasoning for reducing the flow is to reduce the size of the instantaneous water heater.
I agree it would be pertinent to design for the actual flow.
My curiosity now is: ("why are these units operating at 3 GPM when they should perform at .4 GPM?)
More concerning, these are existing units, I have been able to measure the actual flow and can size the instantaneous heater appropriately.
However, how would one size a heater for a new eyewash unit? Mfg literature indicates .4 gpm, but what I see is that this could vary by almost 10x?
For this project I will go back to the site and do some trial and error testing.
RE: Emergency Eye Wash Water Flow
Maybe these did not have them or they were removed during installation.
RE: Emergency Eye Wash Water Flow
http://www.globalindustrial.com/p/safety/eyewash-s...
http://www.eyewashdirect.com/Acorn-S0000-IWH1-Eye-...
I assume that you are trying to supply tepid water for the eyewash stations.
Suggest that you also become familiar with the ANSI standards
http://www.eyewashdirect.com/ANSI-Eyewash-Z358-Eye...
MJCronin
Sr. Process Engineer
RE: Emergency Eye Wash Water Flow
It would be akin to putting a 1.28 GPF flush valve on a water closet design to work with 1.6 GPF. It won't get all the crap out.
RE: Emergency Eye Wash Water Flow
You say you looked at the O&M manual; what was the flow rate specified therein?
TTFN
I can do absolutely anything. I'm an expert!
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers
RE: Emergency Eye Wash Water Flow
If the eye wash is flowing at 3 gpm, the water should be coming out like a fountain.
RE: Emergency Eye Wash Water Flow
Richard A. Cornelius, P.E.
WWW.amlinereast.com
RE: Emergency Eye Wash Water Flow
RE: Emergency Eye Wash Water Flow
MJCronin
Sr. Process Engineer