heat exchanger
heat exchanger
Dear All
Increase in fluids flow rate in heat exchangers increase heat transfer rate we all know. Hot fluid flow rate increase will result in increase in heat transfer rate but when cold fluid flow rate increases heat transfer rate decreases why? I am very much puzzled about it? Please guide me
RE: heat exchanger
If the process is limited by the heat transfer rate on the hot side, and you increase the cold side flow you will have little to no impact on the overall heat transfer. All that will happen is that the cold side fluid will have a lower delta T.
The overall performance will decrease, since you are moving more fluid with no improvement in heat removal.
RE: heat exchanger
Thanks for your reply. I want to know that why this phenomenon happens when we increase cold fluid flow rate.
pradeep
RE: heat exchanger
RE: heat exchanger
Sorry Sir I did not gt your point. Please explain how fouling increase heat transfer rate.
Pradeep
RE: heat exchanger
So you have 7 R's; hot fluid, hot side boundary layer, hot side fouling, tube wall, cold side fouling, cold side boundary layer, cold fluid.
If the first two (or three) are the largest, then changing the last two (or three) will have almost no impact on total heat transfer.
You must understand what is limiting heat transfer before you can change it.
RE: heat exchanger
The overall U is also affected by the hot side bulk to tube wall viscosity ratio - see the Dittus Boelter or Sieder Tate equation for this effect. In layman's terms, the thicker the film layer at the tube wall, the greater the resistance will be to heat transfer.
As the cold side flow increases, the tube wall gets cooler and the film resistance on the hot side increases also due to the increase in hot side wall viscosity. In this case, it may be that the hot fluid viscosity is significantly affected by temp. So overall U drops, since the increase in cold side "h" is damped by the corresponding decrease in hot side "h".
RE: heat exchanger
As georgeverghese explained, if an increase of water flow cools the metal wall and, as a rssult, it increases the viscosity of the oil, reducing its convection heat transfer coefficient "hoil", the overall U will drop.
