hi everybody
i have a structure with 46 ft of clean span i'm using steel beam W24X68 @ 6.5 ft with a steel deck with 2 inch of concrete (composite section)
the live load is 105 lb/ft2, all is checking (deflection, flexure and shear) but i feel this section w24x68 very small for this span
what do you think about this?
i have a structure with 46 ft of clean span i'm using steel beam W24X68 @ 6.5 ft with a steel deck with 2 inch of concrete (composite section)
the live load is 105 lb/ft2, all is checking (deflection, flexure and shear) but i feel this section w24x68 very small for this span
what do you think about this?






RE: Structural opinion about solution
To answer your question though, with composite action, no. You might want to check your response frequency though for vibration response.
Mike McCann, PE, SE (WA)
RE: Structural opinion about solution
RE: Structural opinion about solution
RE: Structural opinion about solution
RE: Structural opinion about solution
I recommend doing a vibration analysis for transient loads. Many times for open, long span floors, we would have to add concrete to dampen down the vibratory response.
RE: Structural opinion about solution
RE: Structural opinion about solution
RE: Structural opinion about solution
How about you respond to the questions and also tell everyone what w deck your using and tech data.
http://www.nceng.com.au/
"Programming today is a race between software engineers striving to build bigger and better idiot-proof programs, and the Universe trying to produce bigger and better idiots. So far, the Universe is winning."
RE: Structural opinion about solution
RE: Structural opinion about solution
RE: Structural opinion about solution
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller