I have designed a fire hydrant system which has water/Foam monitors, spray nozzles, foam chambers and hydrants for a fuel storage tank facility. I came up with a pressure of 9 bars and a flow of 7000 lpm. Please help me properly size the fire pump. The pump shall be a diesel driven centrifugal. Thanks eki19606

RE: Selecting the fire pump

Contact a fire pump supplier with your request. Does the pump have to comply with any particular fire pump code?

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)

RE: Selecting the fire pump

(OP)
Artisi, thanks very much. Well one of the parameter or code of NPFA, if I am on the right track, in fire pump selection is the pump should produce 65% of that pressure which would than be 65% x 9 = 5.85 bar and 150% of the flow which then would be 150% x 7000 = 10500 lpm. Am I going on the right track or? Any suggestion from anyone?

RE: Selecting the fire pump

if you have to comply with NPFA, you will need to open discussions with a firepump supplier / manufacturer who can supply NFPA approved fire pumps. As for applying the NFPA code, there are many steps and loops to jump thru' to meet compliance and if you are asking these basic questions I would suggest you engage a specialist in NFPA systems as peoples lives depend on a properly operating system. And further, if the system has to conform with NPFA normally stipulated by the insurance underwriters there are no short-cut in correct selection and installation.

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources