If OSHA conflicts with IBC which one to use?
Are there industries preferred to use Osha over Ibc, vice versa? Say industrial vs commercial.
Handrail requirement per Ibc is 30 in. OSHA is either 4 or 6 feet.
RE: If OSHA conflicts with IBC which one to use?
So, if you have a stairway at a workplace then you need to have both a continuous handrail with all the handrail requirement (clearance, grab diamemter, no posts, etc.) and you also require a guard rail at 42". If you have a opening or edge which requires fall protection then you only need the 42" guardrail.
Professional and Structural Engineer (ME, NH, MA)
American Concrete Industries
www.americanconcrete.com
1926.501(b)(1)
"Unprotected sides and edges." Each employee on a walking/working surface (horizontal and vertical surface) with an unprotected side or edge which is 6 feet (1.8 m) or more above a lower level shall be protected from falling by the use of guardrail systems, safety net systems, or personal fall arrest systems.
1910.23(c)(1)
Every open-sided floor or platform 4 feet or more above adjacent floor or ground level shall be guarded by a standard railing (or the equivalent as specified in paragraph (e)(3) of this section) on all open sides except where there is entrance to a ramp, stairway, or fixed ladder. The railing shall be provided with a toeboard wherever, beneath the open sides,
(i) Persons can pass,
(ii)There is moving machinery, or
(iii)There is equipment with which falling materials could create a hazard.