Hi,

According to Appendix 8, cm = 1.0 when columns are subjected to transverse loading between supports. What is this transverse loading? What causes transverse loads? Is this from lateral loads (wind/seismic)?

RE: Cm coefficient calculation for B1 multiplier

Correct.

RE: Cm coefficient calculation for B1 multiplier

(OP)
When designing columns that supports the trusses, like moment frame connections, I dont need to treat the the chord compression and tension forces on the column as transverse load right? The cm for those can be calculated using the equation cm = 0.6 - 0.4(M1/M2) correct?


RE: Cm coefficient calculation for B1 multiplier

I would be inclined to use 1.0 unless the column size is becoming troublesome.

RE: Cm coefficient calculation for B1 multiplier

(OP)
Yup, using cm=1.0 gives B1=1.35 which is killing the column. This is under the gravity load case (1.2D + 1.6L) and not even the lateral load case. If I calculate the cm using the equation, it gives me a value of 0.76 and a B1 = 1.0. I dont want to size the column 35% more than what is required.

RE: Cm coefficient calculation for B1 multiplier

Quote (BAGW)

What causes transverse loads? Is this from lateral loads (wind/seismic)?

Gotta be careful with precise definitions. Lateral loads delivered to columns by a typical moment frame beam would not trigger Cm = 1.0. Wind loads delivered to a column by a girt on the other hand would.

Your best litmus test for Cm is as follows:

If your column shear diagram has a discrete step in it, Cm = 1.0. Otherwise, Cm is per the equation.

Quote (BAGW)

When designing columns that supports the trusses, like moment frame connections, I dont need to treat the the chord compression and tension forces on the column as transverse load right? The cm for those can be calculated using the equation cm = 0.6 - 0.4(M1/M2) correct?

The trick here is to recognize that there's an important difference between

a) a case where the lateral load is just a load and;
b) a case where the lateral load is both a load and a lateral restraint.

I've tried to illustrate the difference below. With your truss / moment connection situation, the lateral load is also a lateral restraint (case B). As such you, can calculate cm (and your euler buckling loads) as the worst of these two cases:

1) a column spanning from the base plate to the truss bottom chord with Cm < 1.0 per the equation and a moment at the top.
2) a column spanning from the truss bottom chord to the truss top chord with Cm < 1.0 per the equation and a moment at the bottom.

This should improve things substantially. Naturally, it's business as usual when checking the other column axis.





I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Cm coefficient calculation for B1 multiplier

(OP)
Thanks kootK. That makes perfect sense to me

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources