Coordination Study - Time Current Graph for 3 pole breaker with one or two pole breaker

Coordination Study - Time Current Graph for 3 pole breaker with one or two pole breaker

Coordination Study - Time Current Graph for 3 pole breaker with one or two pole breaker

(OP)
Hello Everyone,

I have a question on TCC when completing a coordination study. Is it correct to show coordination of a 3 pole breaker with a single or two pole breaker. For example a panelboard has a main of 225A and the branch breakers are all single pole 20A. On the TCC is it correct to show how the main coordinates with 20A/1P breaker. If not Why?

RE: Coordination Study - Time Current Graph for 3 pole breaker with one or two pole breaker

Yes, you need to coordinate the three-pole breaker with the single-pole breaker (and can show this on a TCC). The three pole breaker trips all three poles for an overcurrent on a single phase, it does not require all three phases to have an overcurrent. Therefore, if there is a fault downstream of one of the single-pole breakers, one phase of the three-pole breaker will also see this same current and could trip if not coordinated properly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources