TAVRIDA Vacuum Circuit Breaker Close and open immediately

TAVRIDA Vacuum Circuit Breaker Close and open immediately

TAVRIDA Vacuum Circuit Breaker Close and open immediately

(OP)
What might cause the TAVRIDA Vacuum Circuit Breaker 630A when closed, it opens back?

RE: TAVRIDA Vacuum Circuit Breaker Close and open immediately

A standing trip could do that.

RE: TAVRIDA Vacuum Circuit Breaker Close and open immediately

Many breakers also have a manual trip, referred to as a '69' switch in ANSI world. If this is pulled out, or there is a defect in the linkage this could cause issues.

RE: TAVRIDA Vacuum Circuit Breaker Close and open immediately

Does the breaker have a "Trip Free" feature?
If the breaker is in a tripped condition or if a trip signal is present and an attempt is made to close the breaker without first resetting the trip or removing the trip signal, the Trip Free mechanism will discharge the closing stored energy and immediately discharge the opening stored energy. It appears that the breaker has closed and re-opened. However the link to the contacts has been disabled so that although the mechanism operates and it appears that the breaker has closed and opened, the contacts do not close.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: TAVRIDA Vacuum Circuit Breaker Close and open immediately

Isolate the electrical trip power and close the breaker. If the breaker trips, then you have a mechanical problem. If it does NOT trip, then you start the process of isolating each possible electrical trip path.

old field guy

RE: TAVRIDA Vacuum Circuit Breaker Close and open immediately

I am curious from the amp rating of this "circuit breaker" if it is a recloser, perhaps used as a circuit breaker. If that is the case, it may have a single 14-32 pin connector that when disconnected, removes all connections from the device.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources