Transformer protection fusing
2

Transformer protection fusing

Transformer protection fusing

(OP)
I have noticed in a distribution transformer protection, that fuse is always placed on the primary side, why? what happens if fuse is placed only on secondary side? pls clarify..

RE: Transformer protection fusing

Very difficult for a fuse on the secondary to clear a transformer fault.

RE: Transformer protection fusing

(OP)
Hi davidbeach,

Thank you.. Any specific technical justification is there?

RE: Transformer protection fusing

Nope, just some basic physics; fuses don't blow for current that doesn't go through them.

RE: Transformer protection fusing

If the transformer is what I'm looking to protect, it stands to reason that I'm going to place the fuses on the supply side of the breaker, which in the vast majority of cases is the high-voltage side. Only in cases where the supply is from the low-voltage side exclusively, for example in a small isolated system where the transformer is used to step up the generator['s] output voltage for long-distance transmission to the load, would using only low-voltage fuses be of value. If the relative robustness of the connected system vis-à-vis the connected generation is anywhere near unity, fusing on both sides might be of value... but that's just on the face of it, as in such situations it might make more sense to set up the generator relaying to recognize the single-phased condition and separate itself from said transformer.

Hope this helps.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Transformer protection fusing

In general, over-current protection devices (like any fuse) ALWAYS go on the SOURCE side of whatever they are trying to protect.

Otherwise, they would not provide any protection!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources