(OP)
We are renovating an existing greenhouse. The researchers moving into this renovated space require evaporative cooling. This greenhouse, which is divided into two 20' x 33' sections, will have a very short pad-to-fan distance (side wall to opposite side wall). Both ASHRAE and the Nat Greenhouse Mfr Assn (NGMA) recommend a baseline 8 CFM/SF for evaporative cooling airflow. However, the NGMA ventilation white paper requires an additional "velocity adjustment factor" when the pad-to-fan distance is below 100'. In this case that factor is 2.24, which is a significant increase in airflow required.

Which is correct? The pad design is the critical airflow piece. I don't want to over-ventilate such a small space, and pad selection hinges on airflow requirements.

Any ideas or recommendations here?

Thanks in advance.
-Brad

RE: Greenhouse evaporative cooler design question

Consider going with the recommended CFM requirement but calculate the pad areas in relation to the CFM and keep the air velocity across the pads low enough to not create carry over of the water on the pads. If remember it should be below 500 FPM velocity but you should check that number, it has been a while for me.

RE: Greenhouse evaporative cooler design question

I would agree with Rogzog. (over)size your pads to keep the velocity low, thus reducing velocity adjustment factor.
What do the psychrometrics tell you? how close to saturation are you coming off the adiabatic cooler?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources