24vdc Positive grounding

24vdc Positive grounding

(OP)
Is it acceptable in the US for a machine to have the positive terminal grounded on the 24vdc power supply?
The machine was developed in Japan.

Ran into a problem when connecting computer laptop to machine PLC seems to be a ground issue since the laptop
computer uses common (negative) on AC power supply (power plug has ground connection). Grounding issue was overcome by using a computer power supply with no ground on plug to the AC outlet.

RE: 24vdc Positive grounding

If the "machine" requires -24VDC then sure..

Is the power supply part of the machine?
Does the instructions for the machine require an isolated supply?


RE: 24vdc Positive grounding

That is very weird even for a Japanese machine. I think something is wrong. You should contact the maker and ask about that.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 24vdc Positive grounding

A lot of older telephony systems used positive earthed supplies because it prevented corrosion of the metal conductors due to galvanic actvity between the metal and the mass of earth, rather than accelerating corrosion by actively driving the corrosion cell as would happen with a negative earthed system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close