NEMA/NFPA/NEC Standards for Thermal Overload Testing
Quick one for the North American audience:
Are there any standards (NEMA/NFPA/NEC or other) that specify that thermal overloads need to be current injection tested periodically, and/or after replacement?
There are pro's and con's for testing them - pro's are obvious, but the con's are that they may retain some 'thermal memory' (which is really mechanical memory in the fact that the bimetal may not return to the ambient position) - so should they be tested at all?
I am not after the testing method or explanations on how its done, nor Company best practices - that is all clear - it is just specifically about the neccessity, by any governing standards, for testing to be done.
Thanks in advance.
Thanks in advance.
RE: NEMA/NFPA/NEC Standards for Thermal Overload Testing
I have come across NETA 2015 Standards stating the following:
Sec 7.16.1.1.B.4 Test motor protection devices in accordance with manufacturer’s published data. In the absence of manufacturer’s data, use Section 7.9
and
Sec 7.9.1.11 49R Thermal Replica Relay: 1. Determine time delay at 300 percent of setting. 2. Determine a second point on the operating curve.
So this is calling for injection testing, but where is this complementing any of the other Standards like IEEE etc.?
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
I did nearly have an epiphany though - a sudden urge to buy Tulips for the Amine Pump motor, and say that I really do care about him despite the wretched choice of starter protection.