Wood, NDS 1991 table 8.2A bolted connection values - 4 modes listed
I know this is an old reference, but assume newer are similar. In table 8.2A on bolted wood to wood connections, there are four modes listed. I understand the parallel to grain, perpendicular to grain in the side member (parallel in main), and perpendicular to grain in main member (parallel in side. The fourth is labled perpendicular. I assume this is perpendicular to grain in both members, but could not think of an application. Is this correct?
RE: Wood, NDS 1991 table 8.2A bolted connection values - 4 modes listed
In the 2012 edition the table is labeled "11A" but it's the same table with the same values. However, the definition has been updated/corrected to read, "Zperpendicular = nominal lateral design value for a single dowel-type fastener, wood-to-wood, wood-to-metal, or wood-to-concrete connection with wood members(s) loaded perpendicular to grain, lbs"
It's interesting to me that the double-shear table includes no such value. I guess that's because I can envision such an occurrence in single shear (a bolted ledger-board-to-ledger-board-connection, for example, inadvisable though that may be) but I can't envision a practical version of that in double shear.
So, in sum, I think the answer to your question is, "Yes, I believe you are correct."