Shear wall considered as moment frame

Shear wall considered as moment frame

(OP)
Hello,

I`ve got a project that only allow me to put some shear walls in one direction (say Y direction).
My intension is to design the building as dual system in Y direction, but special moment frame in X direction, despite some girders connected to shearwall`s weak axis. Is that legit to considered shearwall in weak axis as column (therefore i could make it as special moment frame).
As we know that seismic reduction factor is diffrent between dual system and moment frame.

thank you, hope you guys can help me.

RE: Shear wall considered as moment frame

(OP)
According ASCE 7-10 R for dual system is 7 while special moment frame is 8.
My project is reinforced concrete building.

RE: Shear wall considered as moment frame

I'm not sure how you combine a shearwall (as a column) with a fixed steel beam connected to it and enter the charts with a concrete/steel combination moment frame. The concern would be the durability and ductility of the connection between the beam and "wall-serving-as-a-column". That configuration isn't a "dual" system by the code I think so you'd have nothing to base the design on.

I suppose you could use the lower R of a steel moment frame vs. a concrete moment frame and go with that.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Shear wall considered as moment frame

I'm going to assume that:

1) We're talking about concrete members for everything here.
2) You're actually planning to have moment frame beam hinges form at the face of the concrete walls.

With that in mind, here are my thoughts:

1) In principle I'm okay with it.
2) You'll need to design your wall convincingly so that it won't yield before the beams form plastic hinges.
3) Whatever you do to the walls to make them work for #2 may affect your over-strength wall flexural capacity in the other direction.
4) If you have to consider a non-orthogonal lateral load case, and I suspect that you do, the accounting associated with looking at the wall for bi-directional lateral load will be a nightmare.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Shear wall considered as moment frame


Quote (KootK)

"We're talking about concrete members for everything here."

I think you may be right - I probably misunderstood the OP

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Shear wall considered as moment frame

(OP)
thanks JAE & KootK.
You`ve got the point about beam hinges moment frame. I just doubt that the wall and beam combination could be considered as special moment frame instead of dual system (walls + frame).
I`ve applied earthquake load in orthogonal direction + rendundancy factor (1.3) + Vertical seismic load (DL + 0.2SDS)
the rebar is pretty crowded, it reach about 3% ratio.

RE: Shear wall considered as moment frame

Hi,

I think you could enlarge the wall´s thickness at the pier legs that way you could direction the efforts to the Piers and your wall in general will be lighter in rebar.

The second thought is about your floor elements, you could use ribbed slabs to distribute evenly the efforts in the weak direction, there is no need to concentrate everything on edges of the wall.

Hope you could figure it out!

Regards,

MSc. Eng. Serguei Joa
Tel: +5352460358
mail: sm.joa@bouygues.cu

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close