Delta Inverter ( Source ) to a TT Grid

Delta Inverter ( Source ) to a TT Grid

Delta Inverter ( Source ) to a TT Grid

(OP)
Hi All

I was wondering what are the limitation regarding the connection of a Delta Connected Inverter ( SMA STP60-10 ) to a TT Grid?

the datasheet and design sheet for the inverter states that it is a Balanced Delta Source with only 3 phase terminals and a PE terminal ,but the electrical company here has some concerns about the reference point since the reference is the neutral line and this inverter does not have one.

so does produce a problem or any concern at all ?

sorry for the long post and thanks alot

RE: Delta Inverter ( Source ) to a TT Grid

You can use three dry type lighting transformers in a wye delta configuration to generate an artificial neutral.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Delta Inverter ( Source ) to a TT Grid

(OP)
Thanks for your reply waross

i know that it is possible to use a wye delta transformer but i wanted to know what is the problem or the consequences of connecting the delta to the TT Grid.

thanks

RE: Delta Inverter ( Source ) to a TT Grid

I would expect that the delta inverter will contribute to the positive sequence loads but that the grid will be the sole supply of the zero sequence component.
I may be wrong. Wait for other posters to confirm this.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Delta Inverter ( Source ) to a TT Grid

Any type of transformer can be use as the utility-DG interconnection transformer. Grounded Wye as the primary on utility side cause desensitize L-G protection if the utility source is weak. Delta on utility side will cause TOV concern on unfaulted phases. Either high current contribution or high voltage contribution, one or the other.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources