Good day everyone, does the ceiling elevation affects the sprinkler area?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
QUESTION: Fire sprinkler area with respect to ceiling elevation
|
RE: QUESTION: Fire sprinkler area with respect to ceiling elevation
If you use QR sprinklers, have light or ordinary hazard and ceilings less than 20', you can reduce the design area per a formula in NFPA 13.
In storage situations, the ceiling height as well as storage height are variables that affect design density.
If you are under FM guidelines, they have criteria based on hazard classification and ceiling height.
Some jurisdictions (I believe Las Vegas, or maybe it is Clark County) require a design area of 10x the ceiling height once you exceed 20'. That is all going from memory so may not be fully accurate.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...
RE: QUESTION: Fire sprinkler area with respect to ceiling elevation
RE: QUESTION: Fire sprinkler area with respect to ceiling elevation
Are you designing to NFPA 13. If so which edition.
RE: QUESTION: Fire sprinkler area with respect to ceiling elevation
If you are using the proper sprinklers, there is a modification that is permitted under NFPA 13 criteria.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...
RE: QUESTION: Fire sprinkler area with respect to ceiling elevation