Hi,
We have a large steam condenser that is running poorly!
The problem:
1) the condenser steam inletcontrol valve goes to 100%
2) the condenser fills with water
3) the outgoing water line that is being heated drops in temperature (because the condenser is full of water)
4) When I open the drain valve on the condenser a large volume of water flows out, then the steam control valves goes back down to 20% and the outgoing water line goes back up to set point
5) The steam trap on the outgoing steam side doesn't seem to be passing steam,
Is the steam trap not functioning correctly? Why does it keep filling with water? I would assume its steam trap related.
Any thoughts? Should we replace the steam trap?
We have a large steam condenser that is running poorly!
The problem:
1) the condenser steam inletcontrol valve goes to 100%
2) the condenser fills with water
3) the outgoing water line that is being heated drops in temperature (because the condenser is full of water)
4) When I open the drain valve on the condenser a large volume of water flows out, then the steam control valves goes back down to 20% and the outgoing water line goes back up to set point
5) The steam trap on the outgoing steam side doesn't seem to be passing steam,
Is the steam trap not functioning correctly? Why does it keep filling with water? I would assume its steam trap related.
Any thoughts? Should we replace the steam trap?
RE: Poor Condenser performance
RE: Poor Condenser performance
We need a diagram and a description of how it is supposed to work.
sounds like level control on your water level isn't working too well from the description you've given.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Poor Condenser performance
Good luck,
Latexman
To a ChE, the glass is always full - 1/2 air and 1/2 water.
RE: Poor Condenser performance
Gabriel Castaneda, P.E.
http://www.gabcheminc.com
RE: Poor Condenser performance
Start with the easy step - open a vent on the steam side at a high point. Let it vent for a few minutes and see if the problem goes away. If so, #4 was the problem. If that doesn't fix the problem, then evaluate the other causes.
RE: Poor Condenser performance
Explained here: http://www2.spiraxsarco.com/resources/steam-engine...
and: http://www.tlv.com/global/TI/steam-theory/stall-ph...
MJCronin
Sr. Process Engineer
RE: Poor Condenser performance
RE: Poor Condenser performance
Hello cal6404,
This is a 'classical' steam problem, and as such interesting, so please respond back, even if you already have found a solution.
As indicated in all answers above, the cause is obviously an imbalance between input and output, which could be caused by malfunctioning equipment, wrong layout in piping, wrongly selected, dimensioned, mounted or placed equipment or input and output regulations working against each other.
For a steam specialist this would be fairly simple to sort out as soon as all details are given.
Good luck.