UPS ROOM AND TRANSFORMER ROOM

UPS ROOM AND TRANSFORMER ROOM

UPS ROOM AND TRANSFORMER ROOM

(OP)
what is the safe air changes in this kind of rooms for exhaust? thanks.

RE: UPS ROOM AND TRANSFORMER ROOM

The amount of air changes required to keep the temperature where you want it.

RE: UPS ROOM AND TRANSFORMER ROOM

As willard says, depends on which part of the world you are from and how much temp rise you can tolerate

RE: UPS ROOM AND TRANSFORMER ROOM

Ensure that you supply the ventilation / cooling system from the generator-backed supply to the UPS, and make sure they automatically re-start after power interruption. It is painful to see the number of UPS installations which overheat and drop the load simply because the room cooling fails.

RE: UPS ROOM AND TRANSFORMER ROOM

you can use 10 ACPH for the UPS room and 5 CFM/kVA of transformer for the transformer room. This is a rule of thumb, you must check with the design engineer for a more accurate answer.

RE: UPS ROOM AND TRANSFORMER ROOM

(OP)
i have a situation where the ups room have transformer. the design using 2 AC (running and back up) to compensate the heat produced by the ups and an exhaust fan added to remove the heat produced by the transformer. my question will be can this design be effective for safe keeping of the equipment?

example:
ups-60KVA (as per catalog it produces 12283.2 btu/hr, so the room needs more than 1TR for cooling, i used wall type AC)
transformer-75KVA (from my calculation at least 400 cfm is need to remove the heat produce by transformer, the exhaust grilles is placed right above the transformer)

thanks

RE: UPS ROOM AND TRANSFORMER ROOM

First of all, it is preferred to keep a positive pressure in the ups. How is air supplied to the room?
You need to account for humidification/dehumidification needs.
If your supply is too cold, it might lead to electrostatic discharge. Be careful when setting the supply temperature.
According to the data you gave us, you also need to increase the cooling load to cover the UPS and the transformer.

RE: UPS ROOM AND TRANSFORMER ROOM

Are the ups and transformer in one room? Why not use only ventilation to remove all the heat?

RE: UPS ROOM AND TRANSFORMER ROOM

For UPS rooms I see two issues:
1) Maintaining suitable room conditions for UPS batteries. In Australia its common for split type DX systems to serve these room. Allowance for 5% of the full battery load is a common conservative figure for preliminary sizing. Batteries are often rated for certain temperatures, in cooler climates its a common oversight to provide cooling only type systems and ignore the fact that batteries take longer to charge when in cold environments.
2) Ventilation of UPS batteries - Many UPS batteries are sealed lead acid types. There are ventilation standards which require minimum ventilation for these types of rooms. Refer to local standards for guidance.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources