water Tank design
water Tank design
(OP)
. also according to our calculation we need around 110 GPM for factory building . please advice how mush will be the tank dimension ? and tank capacity per day ?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: water Tank design
No flow data, no peak flow.
If your feed is good enough, you don't need any tank. If it's bad then you need maybe a days supply.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: water Tank design
In this factory area there is no feed of water from city. Just there we work on under ground tanks. We calculate that factory need 110 GPM from the number of lavatory, shower,sinks and its fixture units. So i calcaculate the water tank size for 8 hr ( 1 shaft). I found it 200 m3. but actually during 8 hr people will nit use all 200 m3. So is there anyway can reduce this 200 m3 to benearst from the size??
RE: water Tank design
I'm guessing that the numbers you used to calculate a design flow were already factored for average usage, so if you provide less than 200 m3 of tankage, you will get an angry phone call some day. ... or your successor will.
Mike Halloran
Pembroke Pines, FL, USA
RE: water Tank design
RE: water Tank design
Instantaneous flow rate would be 50 gpm (2 water closets).
That should get you close.
RE: water Tank design
How did you calculate it?
How many people, how many units, how many take showers, what type of toilet flush.
As said the 110 GPM may well already include for the fact that not all units will operate all the time, but on average over a day they will use that amount.
There are lots of unit calculators around which provide this number.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: water Tank design