Ldh greater than column width
THE CONNECTION BETWEEN COLUMN AND BEAM, IF THE WIDTH OF THE COLUMN PARALLEL TO THE BEAM IS LESS THAN (Ldh) OF THE BEAM what can i do ? Column width could not be change
I have a second question developement length is for no.10 to no.36 what if i have no.40 what Ld be ?
RE: Ldh greater than column width
2) See if you can justify developing your bars for less than Fy.
3) Use alternate anchorage schemes such as headed bar ends.
but in my case
1)i cant use smaller bars
2)As provided = As required
3)for headed bars ldt is greater than my column width .
Here i have a question:
The 90 degree hook length should be min 12db.
Do you know if i can extend this bar ?if yes can you send me the reference please
It depends, in part, on where you practice. In the UK, the concrete code has provisions for extending the hook to get your development. Attention must be paid to the radius in side the bend. In the US, you can use a curved bar node strut and tie model (Link).
Regardless of what you manage to accomplish regarding development of the rebar, you still need to design the joint to transfer the required moment (Link). And, by the sound of it, that's going to be tough given your proportions.
And i really appreciate your help even if i coulnt get the solution thank you a lot
Thanks for the link to the Curved-Bar Node article.
Thank you
Its mentionned in Aci 318M-11 21.7.5.2
Thank you a lot kootk
I checked it out a bit and, to be honest, I don't know the answer to this one. If you look at the non-seismic Ldh requirements, they give you the impression that it's hard to derive any confinement benefit for hooked bars of such a large diameter. So it makes sense to me that ACI would discourage excessively large hooked bars for high seismic applications. I wouldn't think that same logic would apply to straight bars however. Perhaps that is just a vestigial carry over from the fact that Ld is expressed as a multiple of Ldh in chapter 21.
Sorry I'm not able to be more helpful on this one.