Using two sprinkler riser

Using two sprinkler riser

Using two sprinkler riser

(OP)
Good day, i have a question regarding risers, im designing a school having very large total area. it has a open field in the middle so the classroom are located at side of the oval field. the owner whats to have sprinkler protection throughout the campus. i proposed two risers since the area is too big making a very long pipe runs. im asking for pieces of advice how can i design such educational institution having that big area. thanks in advance.

RE: Using two sprinkler riser

One whole building??

Or multiple separate buildings??

Total square feet?

RE: Using two sprinkler riser

(OP)
cdafd

multiple separate building with a corridor connecting it.

TravisMack

can you explain further? btw since the school i just expanding the new fire protection system will be supply by the existing fire pump in the site, having a underground fire mains.

RE: Using two sprinkler riser

""""multiple separate building with a corridor connecting it. ,""""

Will all buildings be sprinkled?

Total sq ft of all old and new??

RE: Using two sprinkler riser

RMERMP

We need the sq ft of each building since NFPA 13 limits coverage to 52k sq. ft. per riser. Provide the info requested by cdafd so we can help you.

RE: Using two sprinkler riser

As long as your system areas are in compliance with NFPA 13, then I envision this:

You have a central pump that is supplying an underground fire main system.

From that underground system, you bring one riser into one building and then the other riser into the building on the other side of the oval field.

I'm sorry, but I don't know how to make it clearer than that without plans and details.

Shoot me something direct via email and I can look at it.

Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources