Forces on single bus bar carrying fault current
Forces on single bus bar carrying fault current
(OP)
How to calculate the forces acting on a single rectangular,grounding bus bar (say 80x6mm ) 200 mm away from ground, running parallel to ground, carrying fault current. I could not find any formula in IEC 60865






RE: Forces on single bus bar carrying fault current
RE: Forces on single bus bar carrying fault current
The magnetic field around a bus bar needs another field to interact with. Not only is the distance squared quite large for current returning through the ground, in the presence of earth of uniform resistivity, the magnetic forces will tend to divert the current through the earth, further increasing the distance squared.
for a very conservative result, consider the fault current to be returning through a bus bar or cable running on the surface of the ground. (Below the crushed gravel layer if this is a sub station.
The result will be quite conservative, however it will give you a safe design figure for the uplifting force on the bus bar supports.
You will be able to verify that the forces will be less than the safe working load on the supports.
Given the distances involved, the forces will be much, much less than the forces during a phase to phase fault.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Forces on single bus bar carrying fault current
RE: Forces on single bus bar carrying fault current