Expansion Joint for R.C.C Structure

Expansion Joint for R.C.C Structure

Expansion Joint for R.C.C Structure

(OP)


I am designing a School Building (R.C.C) Which is 150 ft Long and 38 Feet in width.

do i need a expansion joint for the length of 150 feet of the structure??

can anyone give me any codal reference for that ???

RE: Expansion Joint for R.C.C Structure

Usually for concrete structures we would allow 200 to 240 ft. before an expansion joint.
No code that I know of requires this - just common practice. The AISC steel manual has a small chart near the front that discusses this for steel, concrete, etc.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Expansion Joint for R.C.C Structure

Consider the following:
- If you have a rigid shearwall system in the far corner of the building, then the other corner of the building will have 150 ft of shrinkage and thermal change to accommodate. If you have a flexible frame system centered on your building, then the volume change calculation will only be for half the building length.

I recommend having a look at the volume change calculations and detailing in the PCI manual. There is a lot of forgiveness in a framed reinforced concrete building so I suspect the 150 ft length will not require an expansion joint.

RE: Expansion Joint for R.C.C Structure

You can try looking at Appendix C of ASCE 7-10, which discusses a number of serviceability considerations. I don't believe it gives you hard-and-fast numbers for when you need a joint but it'll at least give you some insight.

RE: Expansion Joint for R.C.C Structure

(OP)
JAE: Thanks for your observation. i will look into The AISC manual.

Teguci: as my building is framed reinforced concrete building so I suspect the 150 ft length will not require an expansion joint.
But i will check the calculations of PCI Manual.

DETstru: yes i have found that Appendix C of ASCE 7-10 but it's just considering the expansion joint thing. not giving any more details.


i have found some guideline in technical Report 65: Expansion Joints in Buildings of The National Academies Press


There i found this Graph which made me understand that, in low temperature difference and length below 200ft a building Need not to be subjected to Expansion joint.

Link: http://www.nap.edu/catalog/9801/expansion-joints-i...



Give me your opinion in this regard.




RE: Expansion Joint for R.C.C Structure

AshiqRumi - that document (graph) you posted is essentially the same graph in the AISC manual.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Expansion Joint for R.C.C Structure

(OP)


JAE: Yes, it is same graph because AISC took it from that Technical Report. (i found it from the reference list of AISC manual)

so i believe this graph is quiet reliable.

do you have any other opinion ?

please share....






Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources