COMBINED STANDPIPE SYSTEM
is FLOOR CONTROL VALVE the same with ‘combination indicating control valve, pressure-reducing valve and check valve.'? which is required in the combined standpipe system.
RE: COMBINED STANDPIPE SYSTEM
http://www.victaulic.com/en/products-services/prod...
What is your section reference out of NFPA 14?
cdafd, the picture you provided is not a floor control valve but a floor manifold. It provides a package drain and flow switch.
Floor control valves on combination systems are normally butterfly valves with internal tamper switches. Sometimes, you will see an OS&Y valve with a tamper switch.
Are you providing Eng drawings or designing this as a project?
4 way FDC is correct for your building (1000gpm). What kind of test connection?
R/
Matt
shall read “COMBINATION STANDPIPE AND TEST CONNECTION”." that in under the Combination Standpipe system. but i think fire service street connections that we are talking about here is somehow a fire hydrant?
btw thanks a lot im learning a lot from you sir.
Missed that
Looked like one a quick glance
The test connection could be for a Fire Pump. Two very separate animals..
R/
Matt
Combination standpipe just means that the vertical pipe serves sprinklers and hose valves. Matt's diagram is perfect for the description. If you have pressure >175 psi, then you need pressure reducing valves. These are often a listed control valve/check valve.
Travis Mack
MFP Design, LLC
www.mfpdesign.com
"Follow" us at https://www.facebook.com/pages/MFP-Design-LLC/9221...