Proprietary Bag Concrete
Looking for some unbiased resources that discusses the problems with proprietary bag concrete.
Some of our contractors want to exclusively use non-Portland cement concrete mixes such as Quikrete and Rapidset. A few engineers I know have an aversion to allowing non-Portland cement, but I have been unconvinced by their argument thus far.
"It is imperative Cunth doesn't get his hands on those codes."
RE: Proprietary Bag Concrete
Quikrete uses portland cement for its concrete mixes. RapidSet uses calcium sulfoaluminate cement for its fast setting products.
For small applications of patching or similar, either would suffice. Weathering resistance is going to be higher with straight portland cement mixtures than CSA cement as CSA cements produce calcium sulfate (gypsum) in the hydration process.
Avoid CSA cements for exterior application because of durability issues.
One specific example of these was the demo of the middle strip of a one-way PT slab (interior) for a new stair. The edge of the opening had to be reinforced to transfer the stair loads to the banded PT runs and support the stair railing, etc - and then obviously poured back in place (about 2 cub.yards). We spec'd USCP HP bag mix, and the contractor decided they wanted to switch to Quikrete's high early strength, because of the most less stringent water requirements (I think the HP is 2.75 quarts/sack and the Quikrete was something like 4 quarts/sack). And - of course it is wayyy cheaper. Of sort of a side note, their labor was not very good at mixing the lower water USCP. They either had dry clumps or lean slop and didn't seem to give a care for adherence to the product instructions. Regardless of the bag mix, we were taking oodles of cylinders out of concern for workmanship.
Thanks for the info on the gypsum!
Though, it may be too dated as of 2016.
Mike McCann, PE, SE (WA)
Also I used it for a leveling topping over an existing slab. Used to come in 60 and 80# bags. Latest is 50#.
One recent project using RAPIDSET involved detensioning 50% of banded PT tendons anchorages to remove large voids/rock pockets due to terrible compaction practices by the concrete crew for a podium slab. Using CSA-based cements enabled us to restress the tendons the same day, then destress the adjacent 50% of tendons, and repeat the process, in a total of 8 hours, and return to service.
Pre-packaged concrete has its place in 'structural concrete', but the site personnel have to be clued in on the water content, admixture use, and in the case of CSA-cement, set time!
DOT's around the US use CSA concrete for pavement and bridge deck repairs, typically 60 lb bags for small quantities, and volumetric mixers for larger volumes.
On the negative side of pre-packaged products, I recently saw a local project where a Sika concrete product in 60 lb bags was used for full depth slab replacement to a parking deck, on a per bay basis of 10'x30'. The contractor 'lost control' of site production with inadequate sized mix equipment, too much mix water, and too few site personnel, resulting in all sorts of shrinkage cracking.