Hi,

I have a 3 electrical boards (3phase 380/230) to feed from a substation.

Electrical Board 1:
S=46KVA
Electrical Board 2:
S=46KVA
Electrical Board 3:
S=120KVA

The current that each eletrical board will "consume" is calculated by:

I = S/(sqrt 3 *400)

Is this correct?

RE: Feeder current

Where'd the 400 come from?

RE: Feeder current

380/230V does not equate.
Possibly 400/230V?????

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Feeder current

(OP)
Hi,

The voltage level is 230/400.

it comes from a feeder located in a private substation.

rgds

RE: Feeder current

(KVA x 1000) / (400V x 1.73) = A
(KVA x 1000) / (230V x 3) = A

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Feeder current

(OP)
Tx to all for the support

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources