2012IBC Table 601 footnote b.

2012IBC Table 601 footnote b.

(OP)
Please help me to understand this footnote b in table 601.
"Except in Group F-1, H, M and S-1 occupancies, fire protection of structural members shall not be required, including protection of roof framing and decking where every part of the roof construction is 20 feet or more above any floor immediately below. Fire-retardant-treated wood members shall be allowed to be used for such unprotected members." note b, Table 601.
1-Does that mean other groups such as (A-4 occupancy) does not require fire protection even if the height is less than 20 ft?
2-Does that means group F-1,H,M,S-1 does not require fire protection if height is more that 20 ft?
Thanks in advance.

RE: 2012IBC Table 601 footnote b.

Zeeko,

I would read this as follows:

1) Your A-4 Occupancy would require a fire-rated ceiling/Floor assembly if the height is less than 20 feet above the floor below.
2) F-1, H, M, S-1 uses would always be required to have a fire-rated assembly with duration as indicated by the table.

EIT, Modular Building Industry

RE: 2012IBC Table 601 footnote b.

(OP)
Warhamer,
Thank you very much for sharing your understanding. When the code start saying "including protection .... etc" I thought the code referring to F-1, H, M, S-1.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close