Can a fixed support for fire pro be use as support for other piping? thanks.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Hangers and supports
RE: Hangers and supports
5 times the weight plus 250 pounds for sprinkler piping. 1.5 times the weight of the other systems using the "Shared Support", all certified by a registered P.E.
Reference 9.1 in the 13 edition of 13.
RE: Hangers and supports
Or does it just seem that way? semantics
9.1.1.3.1.1 Sprinkler pipe and other distribution systems shall be permitted to be supported from a shared support structure designed to support five times the weight of water-filled sprinkler pipe and other supported distribution systems plus 250 lb (115 kg), based on the allowable ultimate stress.
9.1.1.3.1.2 Sprinkler pipe and other distribution systems shall be permitted to be supported from a shared support structure designed to support five times the weight of the water-filled sprinkler pipe plus 250 lb (115 kg), and one and one-half times the weight of all other supported distribution systems.
RE: Hangers and supports
It confused me as well.
It seems you either do #1 or #2. #1 being worse.
We went with #2 from the Structural Engineer.
R/
Matt
RE: Hangers and supports