I am referring to the 1/2" ball valves typically found in the trim of Alarm\Dry\Deluge valves. NFPA 13, 2013 8.17.1.4 states that these valves should be sealed, locked, or electronically supervised. These are almost always 1/2" ball valves, and I don't think any of them are lockable ball valves, so how would the supervision be accomplished?

RE: Alarm Line Control Valve

Drill a hole in the handle and install a plastic tie, lock, or install electronic supervision. The other option is to remove the valve all together.

I believe Potter sells a electronic 1/2" valve. The problem if the valve is closed no water gos to the flow switch and the central station. Can not tell u how many I have found closed.

RE: Alarm Line Control Valve

(OP)
Thanks, LCREP. Your first option is the one I came up with too. It seems like the alarm valve manufacturers would have addressed this already.

RE: Alarm Line Control Valve

Victalic has they have removed the shut off valve to the pressure switch.

RE: Alarm Line Control Valve

(OP)
On Vic's wet system alarm valves, they still have the 1/2 normally open valve in the trim. Viking is this way also. I didnt look at any other manufacturer.

CDAFD, that second option looks like a reasonable alternative, thanks.

RE: Alarm Line Control Valve

""""Vic's wet system alarm valves, they still have the 1/2 normally open valve in the trim"""""

What does it go to???

RE: Alarm Line Control Valve

It is the dry, pre action and deluge valve I am concerned with since a vain water flow device can not be used. Wet system most of the newer stuff I see has a vain transmitter few have water motor gong with a pressure switch on the top of the retard chamber. If they do then yea you have the same problem.

I think I recall the IBC does not require the 1/2" valve to be supervised, never understood why they gave the exception, makes no sense to be given how many times I found them closed.

RE: Alarm Line Control Valve

There should be no shut off valve in the piping for the high pressure/flow switch!!

RE: Alarm Line Control Valve

Nope

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources